Search found 13 matches

by olliew
16 Oct 2024, 11:14
Forum: Specific Test Case Questions
Topic: ETS TEDCheck Test Failed
Replies: 4
Views: 450

Re: ETS TEDCheck Test Failed

Hello Profinet Experts, I am working on pre-testing my PROFINET device. I received the GSDML file from the vendor and modified it according to my needs. I am using an ETS test setup with ART tester version 2.45.0.2. While performing TEDcheck (CLPRC), the test failed with the following error: "...
by olliew
16 Oct 2024, 10:57
Forum: Test Preparation
Topic: Does ETS-Board is necessary for PN pretesting?
Replies: 2
Views: 308

Re: Does ETS-Board is necessary for PN pretesting?

sagar.dukare wrote: 16 Oct 2024, 07:37 I found the PN test bundle on PI website.
In the test bundle look for test specification Testspec-PN_2572_V245_Jun24.pdf.
Chapter 5.5.5 table 5-22 lists the tests and required test setup.
Except for InterOp tests, all tests are run using the ETS test setup.
by olliew
25 Jun 2024, 11:48
Forum: PROFINET Implementation
Topic: "Invalid login or password." at "https://gitlab.profibus.com/"
Replies: 5
Views: 5235

Re: "Invalid login or password." at "https://gitlab.profibus.com/"

Screenshot 2024-06-25 114609.png
Screenshot 2024-06-25 114609.png (13.17 KiB) Viewed 5216 times

Did you try Request Access?
by olliew
25 Jun 2024, 07:58
Forum: PROFINET Implementation
Topic: "Invalid login or password." at "https://gitlab.profibus.com/"
Replies: 5
Views: 5235

Re: "Invalid login or password." at "https://gitlab.profibus.com/"

Hello: Even though I am a registered member of the PI, and am able to download from the profibus.com all available materials, today I tried to access https://gitlab.profibus.com/ , but I was not successful. I get "Invalid login or password. " error. I no not want to reset the password, ho...
by olliew
22 Apr 2024, 08:35
Forum: Basics
Topic: Does PROFINET have a similar mechanism to SystemCommand?
Replies: 1
Views: 4089

Re: Does PROFINET have a similar mechanism to SystemCommand?

Does PROFINET have a similar mechanism to SystemCommand? Yes and No. Since there are differing 'categories' of IO-Link SystemCommands, some have an equivalent in PROFINET and some do not. For example the IO-Link factory settings is a DCP ResetToFactory service in PROFINET. The big difference is tha...
by olliew
08 Mar 2024, 15:37
Forum: Test Preparation
Topic: Profinet test bundle
Replies: 3
Views: 301

Re: Profinet test bundle

Hi Team, We have the latest test bundle from PI that is 2.44.1.2. My query here is are all the test cases migrated from standard setup to ETS setup i.e. unified test setup, if no when it will be done? Moving further if we want to certify our profinet device the pre-test execution should be sufficie...
by olliew
08 Mar 2024, 15:15
Forum: PROFINET Implementation
Topic: Demo application on top of Profinet and Profidrive
Replies: 1
Views: 3730

Re: Demo application on top of Profinet and Profidrive

To do a read / write PROFIdrive PNU object you use the SINAPARA function block (FB286) which is part of the SINAMICS library. IIRC that comes with TIA Portal per default. In TIA Portal the help is slightly misleading, the function block works just fine with any PROFIdrive compliant device. So, do yo...
by olliew
13 Feb 2024, 13:12
Forum: PROFINET Implementation
Topic: Problem with device identity
Replies: 3
Views: 5766

Re: Problem with device identity

Mich_P wrote: 12 Feb 2024, 09:56 I always get device mismatch error from the controller and connection establishment is not successful.
Maybe a mismatch in API number?
A wireshark inspection of the Connect Request and Connect Response should point to the exact subslot position of the mismatch.
by olliew
29 Jan 2024, 13:24
Forum: PROFIenergy
Topic: Source code example
Replies: 2
Views: 7917

Mich_P wrote: 18 Jan 2024, 14:55 Is there any source code example available for the implementation of PROFIenergy on a Profinet device?
There is no PROFIenergy community example.
The stack providers may have an example implementation, if you already use a device stack you can ask your provider.
by olliew
29 Jan 2024, 11:59
Forum: Specific Test Case Questions
Topic: Unexpected LLDP frame from "PROFIBUS" TLV?
Replies: 6
Views: 500

Re: Unexpected LLDP frame from "PROFIBUS" TLV?

The primary setup tool may install those, not sure.
Do the LLDP frames disappear when you disable PROFINET IO protocol (DCP/LLDP) ?
by olliew
29 Jan 2024, 11:52
Forum: PROFIenergy
Topic: Light curtain with Profinet
Replies: 2
Views: 8691

L_zea wrote: 25 Jan 2024, 09:19 I’m implementing a light curtain with Profinet. Does it make sense to support also Profienergy for such a device?
hello L_zea,

I think it makes sense.
Even when energy savings for a single device may be 'low', it is the amount of devices that count :)
by olliew
08 Oct 2023, 08:06
Forum: PROFIdrive
Topic: Profidrive on both RT and IRT
Replies: 2
Views: 14272

sayed15 wrote: 05 Oct 2023, 21:06 Can the Profidrive profile be utilized on both Profinet RT and IRT technologies ?​
Yes. Some of the application classes require IRT though.
by olliew
08 Oct 2023, 08:04
Forum: PROFIdrive
Topic: Profidrive application classes
Replies: 3
Views: 13147

What are the available Profidrive Application Classes ? Standard Drive Standard drive with distributed technology controller Single axis positioning drive, with local Motion Control Motion Control with central interpolation and speed setpoint interface Motion Control with central interpolation and ...