Search found 15 matches
- 24 Nov 2025, 15:32
- Forum: Specific Test Case Questions
- Topic: In ETS Test Setup, the PROFIsafe tests are sometimes successful, sometimes failed - Why?
- Replies: 1
- Views: 8227
Re: In ETS Test Setup, the PROFIsafe tests are sometimes successful, sometimes failed - Why?
In ETS Test Setup, the PROFIsafe tests are sometimes successful, sometimes failed (if repeated without changing anything). The failure is due to PROFIsafe watchdog expiration. What could be the reason for this instable behavior? Without having further details, it might be due to an F_WD_Time settin...
- 14 Oct 2025, 09:59
- Forum: PROFIsafe
- Topic: Multiple PROFIsafe submodules and ART-Tester
- Replies: 2
- Views: 25388
Re: Multiple PROFIsafe submodules and ART-Tester
Hello, we created a device that implements several PROFIsafe submodules. These submodules are combined in one PROFIsafe module using the attributes "PhysicalSubslots" and "FixedInSubslots" Example: <ModuleList> <ModuleItem ID="IDM_1" ModuleIdentNumber="0x00000001&...
- 16 May 2025, 09:43
- Forum: Specific Test Case Questions
- Topic: Spirta + CP1616 testing - Synchronous AR
- Replies: 1
- Views: 42471
Re: Spirta + CP1616 testing - Synchronous AR
Hello, We have a drive connected to a PC equipped with CP1616 and Spirta. We bought the CP1616 to test the drive before going to a PROFINET lab and try the certification (RT and IRT). I was expecting Spirta to establish a synchronous communication with the drive (for example in test Syncslave01_WFU...
- 16 May 2025, 09:38
- Forum: Security and Certification
- Topic: P2P-Setup Tests for Certification mandatory?
- Replies: 1
- Views: 79755
Re: P2P-Setup Tests for Certification mandatory?
Hello everyone, in which cases are the tests with P2P-Setup mandatory? Are these testcases required for certification with 2 or more port devices? (Especially "Different Access Ways P2P" because in list of test specification these test is not listed (Pn-Spec 2021)) Thanks for your answers...
- 16 May 2025, 09:35
- Forum: Specific Test Case Questions
- Topic: SL1 Device Test Fail-conditions
- Replies: 1
- Views: 27230
Re: SL1 Device Test Fail-conditions
Hello everyone, if have a simple question. Did the test fail in Faulty and Normal mode if one of the two output bits "Qx_Error.." is set? I ran the test with a new device and after the test the device works fine, but the error bits were set in Faulty Mode. (Test was executed with specific...
- 09 Apr 2025, 09:13
- Forum: Specific Test Case Questions
- Topic: AR-ASE S2 test failed
- Replies: 3
- Views: 92663
Re: AR-ASE S2 test failed
Hello, I need a helping hand concerning above mentioned test. My device is failing when I run AR-ASE S2 test, in the beginning of Scenario 1-4. Behavior 8, 9, 10 and 11, right in the sequence, are failing as well. AR-ASE and other behavior tests are ok. Log shows the following messages: 14:40:11 - ...
- 26 Mar 2025, 09:59
- Forum: Specific Test Case Questions
- Topic: AR-ASE S2 test failed
- Replies: 3
- Views: 92663
Re: AR-ASE S2 test failed
Hello, I need a helping hand concerning above mentioned test. My device is failing when I run AR-ASE S2 test, in the beginning of Scenario 1-4. Behavior 8, 9, 10 and 11, right in the sequence, are failing as well. AR-ASE and other behavior tests are ok. Log shows the following messages: 14:40:11 - ...
- 13 Dec 2024, 12:58
- Forum: PROFIsafe
- Topic: PROFIsafe Watchdog tolerance
- Replies: 8
- Views: 1813505
Re: PROFIsafe Watchdog tolerance
Hey Daniel, thank you for your answer! How are the wd_min and wd_max values measured in detail? Is the watchdog started and then monitored cyclically to determine whether it has been triggered? (wd_max) And how is the wd_min value measured? Thank you very much in advance for your answer! Hi Booster...
- 02 Dec 2024, 09:24
- Forum: PROFIsafe
- Topic: PROFIsafe Watchdog tolerance
- Replies: 8
- Views: 1813505
Re: PROFIsafe Watchdog tolerance
Hi Booster, no these are two different Times. The Device-Cycle-Time is the cycle time the time the device communicates with the F-Host e.g. 1ms. The Device-Acknowledgment-Time is the time the device needs to react on a changed MonitoringNumber (MNR). There is no other time included such as transmis...
- 28 Nov 2024, 12:47
- Forum: PROFIsafe
- Topic: PROFIsafe Watchdog tolerance
- Replies: 8
- Views: 1813505
Re: PROFIsafe Watchdog tolerance
The PROFIsafe Tests include tests with the Safetylayer-Tester. In documentation of Safetylayer-Tester, the watchdog test is required for certification. It should be checked whether the measured times are within tolerance. Maximum value = ((watchdog value + 10%) + device cycle time + inaccuracy of m...
- 27 Nov 2024, 13:46
- Forum: PROFIsafe
- Topic: PROFIsafe Watchdog tolerance
- Replies: 8
- Views: 1813505
Re: PROFIsafe Watchdog tolerance
The PROFIsafe Tests include tests with the Safetylayer-Tester. In documentation of Safetylayer-Tester, the watchdog test is required for certification. It should be checked whether the measured times are within tolerance. Maximum value = ((watchdog value + 10%) + device cycle time + inaccuracy of m...
- 18 Jul 2024, 14:49
- Forum: PROFIsafe
- Topic: How to differentiate between Profinet and Profisafe messages?
- Replies: 2
- Views: 42319
Re: How to differentiate between Profinet and Profisafe messages?
Hi Forum, My task: I am supposed to filter incoming/outgoing Profinet and Profisafe messages from a safety PLC (probably SIEMENS 15xx series) in a so-called "APL module" and incorporate them into a new frame. The black channel comes to the APL module via Ethernet APL and should now be for...
- 10 Oct 2023, 11:45
- Forum: Process - Certification "How to"
- Topic: Validity period of the Profinet certificate
- Replies: 3
- Views: 38807
- 10 Oct 2023, 11:38
- Forum: Process - Certification "How to"
- Topic: Changes allowed without triggering recertification
- Replies: 1
- Views: 30085
What modifications to an already certified Profinet device are permitted without necessitating the recertification process again ? If the modifications have no influence to the communication a recertification is not necessary. But you need extend your certificate to the new Software Version via a v...
- 09 Oct 2023, 13:57
- Forum: Process - Certification "How to"
- Topic: Vendor and Device ID
- Replies: 4
- Views: 46551
How can I acquire a vendor ID for my device ? You can acquire your vendor ID directly at the PI Office. Just write them an e-mail with your request and they will help you. PROFIBUS Nutzerorganisation e.V. (PNO) Ohiostr. 8 76149 Karlsruhe Tel.: +49 721 986 197 42 Fax: +49 721 986 197 11 certificati...