Hello everyone,
I have a question about the non-profinet-neighbor test cases with the ETS board (ART tester version 2.44.1.2)
If I have understood the test specification correctly, the non-profinet neighbors are simulated. So no additional hardware is required.
With the current ART-Tester version, the tests failed in my case. But the execution with ART-Tester version 2.42.xx passed...
The following error code is coming: "Error: lldpRemChassisID '08' does not match value from neighbor '08-00-00-00-00-01'"
Is additional configuration required or is the cabling possibly incorrect? Currently only the lower ports of IF1 and IF2 and the Ctrl_IF are wired.
Many thanks in advance for the answers!
Non-Profinet-neighbor Testcases with ETS-Board
Re: Non-Profinet-neighbor Testcases with ETS-Board
The test coverage was increased in the meantime. It is possible that this is an issue in your implementation which was not uncovered by older version of ART.Booster wrote: ↑05 Mar 2024, 14:02 Hello everyone,
I have a question about the non-profinet-neighbor test cases with the ETS board (ART tester version 2.44.1.2)
If I have understood the test specification correctly, the non-profinet neighbors are simulated. So no additional hardware is required.
With the current ART-Tester version, the tests failed in my case. But the execution with ART-Tester version 2.42.xx passed...
The following error code is coming: "Error: lldpRemChassisID '08' does not match value from neighbor '08-00-00-00-00-01'"
Is additional configuration required or is the cabling possibly incorrect? Currently only the lower ports of IF1 and IF2 and the Ctrl_IF are wired.
Many thanks in advance for the answers!
Re: Non-Profinet-neighbor Testcases with ETS-Board
Thank you for your answer!benja_m wrote: ↑06 Mar 2024, 07:50The test coverage was increased in the meantime. It is possible that this is an issue in your implementation which was not uncovered by older version of ART.Booster wrote: ↑05 Mar 2024, 14:02 Hello everyone,
I have a question about the non-profinet-neighbor test cases with the ETS board (ART tester version 2.44.1.2)
If I have understood the test specification correctly, the non-profinet neighbors are simulated. So no additional hardware is required.
With the current ART-Tester version, the tests failed in my case. But the execution with ART-Tester version 2.42.xx passed...
The following error code is coming: "Error: lldpRemChassisID '08' does not match value from neighbor '08-00-00-00-00-01'"
Is additional configuration required or is the cabling possibly incorrect? Currently only the lower ports of IF1 and IF2 and the Ctrl_IF are wired.
Many thanks in advance for the answers!
I was a little confused because the test cases are normally categorized into the required test setup groups.
For example, the non-Profinet-neighbor test cases are not assigned to the ETS test setup, but to a non-Profinet-neighbor-setup.
But thanks for the hint anyway! I will check it again after implementation.