Help Needed with Pre-Testing Two-Port PROFINET Device Configuration

yasiralismb1
Posts: 3
Joined: 10 Sep 2024, 10:28

Help Needed with Pre-Testing Two-Port PROFINET Device Configuration

Post

Hi everyone,

I am currently pre-testing a two-port PROFINET device before applying for the actual certification in the lab. I am using an ETS board for testing and following the steps outlined in the product documentation.

Here is what I have done so far:

Set the IP for the NIC connected to the ETS as 192.168.5.2, and communication with the ETS board is working.
Set the IP of the PROFINET device to 192.168.0.50 as per the documentation.
However, the BF LED on the PROFINET card keeps blinking, indicating that there is likely a configuration issue.

Could someone guide me on the correct way to configure the IPs or point out any steps I might be missing? Any advice on correctly setting up each part of the system would be greatly appreciated
benja_m
Posts: 25
Joined: 06 Oct 2023, 09:24

Re: Help Needed with Pre-Testing Two-Port PROFINET Device Configuration

Post

yasiralismb1 wrote: 12 Sep 2024, 17:05 Hi everyone,

I am currently pre-testing a two-port PROFINET device before applying for the actual certification in the lab. I am using an ETS board for testing and following the steps outlined in the product documentation.

Here is what I have done so far:

Set the IP for the NIC connected to the ETS as 192.168.5.2, and communication with the ETS board is working.
Set the IP of the PROFINET device to 192.168.0.50 as per the documentation.
However, the BF LED on the PROFINET card keeps blinking, indicating that there is likely a configuration issue.

Could someone guide me on the correct way to configure the IPs or point out any steps I might be missing? Any advice on correctly setting up each part of the system would be greatly appreciated
Assuming the blinking LED "simply" indicates that no cyclic communication is in place, this seems plausible.
ETS only established a connection when a test is performed. And not all tests require a connection, esp. most of the DCP testcases for example do not establish a connection.

Does the LED behavior change when you execute different testcases?
yasiralismb1
Posts: 3
Joined: 10 Sep 2024, 10:28

Re: Help Needed with Pre-Testing Two-Port PROFINET Device Configuration

Post

benja_m wrote: 12 Sep 2024, 18:51
yasiralismb1 wrote: 12 Sep 2024, 17:05 Hi everyone,

I am currently pre-testing a two-port PROFINET device before applying for the actual certification in the lab. I am using an ETS board for testing and following the steps outlined in the product documentation.

Here is what I have done so far:

Set the IP for the NIC connected to the ETS as 192.168.5.2, and communication with the ETS board is working.
Set the IP of the PROFINET device to 192.168.0.50 as per the documentation.
However, the BF LED on the PROFINET card keeps blinking, indicating that there is likely a configuration issue.

Could someone guide me on the correct way to configure the IPs or point out any steps I might be missing? Any advice on correctly setting up each part of the system would be greatly appreciated
Assuming the blinking LED "simply" indicates that no cyclic communication is in place, this seems plausible.
ETS only established a connection when a test is performed. And not all tests require a connection, esp. most of the DCP testcases for example do not establish a connection.

Does the LED behavior change when you execute different testcases?

Yes you are right when ETS board communicate with it BF led stop blinking. I configured my device according to ProductDocumentation.pdf guidlines, I can access ETS board in ART-Tester but I have some DCP test failed. DCP_1 logs is following.

18:57:28 - Starting Testcase: DCP - DCP 1
18:57:28 - Initializing Power Outlet
18:57:30 - DCP_1: Start of test DCP - DCP 1 without VLAN-Tag
18:57:30 - DCP_1: Test step 1: Requesting ResetToFactory (reset communication parameters) of the dut
18:57:30 - DCP_1: Test step 2: Waiting for the DUT to apply the reset to factory request. [ms]: 60000
18:58:30 - DCP_1: Test step 3: Check the IdentifyAll response behavior.
18:58:30 - DCP_1: Test step 4: Powering off - on the dut
18:58:36 - DCP_1: Test step 5: Waiting for the DUT to power up again.
19:00:08 - DCP_1: Test step 6: Set the name of station to 'dut' permanently.
19:00:13 - DCP_1: Test step 7: Send an Identify.Req with the name of the DUT as filter.
19:00:13 - DCP_1: Test step 8: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:00:18 - DCP_1: Test step 9: Send a DcpGet.Req with the following parameter: NameOfStation, DeviceId, MacAddress and IpParamter.
19:00:18 - DCP_1: Test step 10: Set the name of station to 'dut' permanently.
19:00:23 - DCP_1: Test step 11: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:00:28 - DCP_1: Test step 12: Requesting ARP for IP - Address: 192.168.0.50
19:00:28 - DCP_1: Test step 13: Check the IdentifyAll response behavior.
19:00:28 - DCP_1: Test step 14: Temporarily set the ip address of the DUT to 192.168.0.51
19:00:33 - DCP_1: Test step 15: Requesting ARP for IP - Address: 192.168.0.51
19:00:33 - DCP_1: Test step 16: Check the IdentifyAll response behavior.
19:00:33 - DCP_1: Test step 17: Powering off - on the dut
19:00:39 - DCP_1: Test step 18: Waiting for the DUT to power up again.
19:02:11 - DCP_1: Test step 19: Requesting ARP for IP - Address: 192.168.0.50
19:02:11 - ERROR: Dcp: No response received.
19:02:11 - ERROR: DCP_1: Test step 20: There was an ARP received. This was not expected.
19:02:11 - DCP_1: Test step 20: DCP - DCP 1: Aborted due to errors.
19:02:11 - DCP_1: Start of test DCP - DCP 1 with VLAN-Tag
19:02:11 - DCP_1: Test step 1: Requesting ResetToFactory (reset communication parameters) of the dut
19:02:11 - DCP_1: Test step 2: Waiting for the DUT to apply the reset to factory request. [ms]: 60000
19:03:11 - DCP_1: Test step 3: Check the IdentifyAll response behavior.
19:03:11 - DCP_1: Test step 4: Powering off - on the dut
19:03:17 - DCP_1: Test step 5: Waiting for the DUT to power up again.
19:04:49 - DCP_1: Test step 6: Set the name of station to 'dut' permanently.
19:04:54 - DCP_1: Test step 7: Send an Identify.Req with the name of the DUT as filter.
19:04:54 - DCP_1: Test step 8: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:04:59 - DCP_1: Test step 9: Send a DcpGet.Req with the following parameter: NameOfStation, DeviceId, MacAddress and IpParamter.
19:04:59 - DCP_1: Test step 10: Set the name of station to 'dut' permanently.
19:05:04 - DCP_1: Test step 11: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:05:09 - DCP_1: Test step 12: Requesting ARP for IP - Address: 192.168.0.50
19:05:09 - DCP_1: Test step 13: Check the IdentifyAll response behavior.
19:05:09 - DCP_1: Test step 14: Temporarily set the ip address of the DUT to 192.168.0.51
19:05:14 - DCP_1: Test step 15: Requesting ARP for IP - Address: 192.168.0.51
19:05:14 - DCP_1: Test step 16: Check the IdentifyAll response behavior.
19:05:14 - DCP_1: Test step 17: Powering off - on the dut
19:05:20 - DCP_1: Test step 18: Waiting for the DUT to power up again.
19:06:52 - DCP_1: Test step 19: Requesting ARP for IP - Address: 192.168.0.50
19:06:52 - ERROR: Dcp: No response received.
19:06:52 - ERROR: DCP_1: Test step 20: There was an ARP received. This was not expected.
19:06:52 - DCP_1: Test step 20: DCP - DCP 1: Aborted due to errors.
19:06:58 - Finished test case DCP - DCP 1.
19:07:02 - Starting Testcase: DCP - DCP_2
19:07:02 - Initializing Power Outlet
19:07:04 - DCP_2: Start of test DCP - DCP_2 without VLAN-Tag
19:07:04 - DCP_2: Test step 1: Requesting ResetToFactory (reset communication parameters) of the dut
19:07:04 - DCP_2: Test step 2: Waiting for the DUT to apply the reset to factory request. [ms]: 60000
19:08:04 - DCP_2: Test step 3: Check the IdentifyAll response behavior.
19:08:04 - DCP_2: Test step 4: Powering off - on the dut
19:08:10 - DCP_2: Test step 5: Waiting for the DUT to power up again.



I do not know why its not getting response of ARP command. normally when i create project in ART-Tester it can automatically get Mac address of DUT.
j.rost
PROFINET Expert
Posts: 10
Joined: 20 Sep 2023, 14:57

Re: Help Needed with Pre-Testing Two-Port PROFINET Device Configuration

Post

yasiralismb1 wrote: 16 Sep 2024, 19:18
benja_m wrote: 12 Sep 2024, 18:51
yasiralismb1 wrote: 12 Sep 2024, 17:05 Hi everyone,

I am currently pre-testing a two-port PROFINET device before applying for the actual certification in the lab. I am using an ETS board for testing and following the steps outlined in the product documentation.

Here is what I have done so far:

Set the IP for the NIC connected to the ETS as 192.168.5.2, and communication with the ETS board is working.
Set the IP of the PROFINET device to 192.168.0.50 as per the documentation.
However, the BF LED on the PROFINET card keeps blinking, indicating that there is likely a configuration issue.

Could someone guide me on the correct way to configure the IPs or point out any steps I might be missing? Any advice on correctly setting up each part of the system would be greatly appreciated
Assuming the blinking LED "simply" indicates that no cyclic communication is in place, this seems plausible.
ETS only established a connection when a test is performed. And not all tests require a connection, esp. most of the DCP testcases for example do not establish a connection.

Does the LED behavior change when you execute different testcases?

Yes you are right when ETS board communicate with it BF led stop blinking. I configured my device according to ProductDocumentation.pdf guidlines, I can access ETS board in ART-Tester but I have some DCP test failed. DCP_1 logs is following.

18:57:28 - Starting Testcase: DCP - DCP 1
18:57:28 - Initializing Power Outlet
18:57:30 - DCP_1: Start of test DCP - DCP 1 without VLAN-Tag
18:57:30 - DCP_1: Test step 1: Requesting ResetToFactory (reset communication parameters) of the dut
18:57:30 - DCP_1: Test step 2: Waiting for the DUT to apply the reset to factory request. [ms]: 60000
18:58:30 - DCP_1: Test step 3: Check the IdentifyAll response behavior.
18:58:30 - DCP_1: Test step 4: Powering off - on the dut
18:58:36 - DCP_1: Test step 5: Waiting for the DUT to power up again.
19:00:08 - DCP_1: Test step 6: Set the name of station to 'dut' permanently.
19:00:13 - DCP_1: Test step 7: Send an Identify.Req with the name of the DUT as filter.
19:00:13 - DCP_1: Test step 8: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:00:18 - DCP_1: Test step 9: Send a DcpGet.Req with the following parameter: NameOfStation, DeviceId, MacAddress and IpParamter.
19:00:18 - DCP_1: Test step 10: Set the name of station to 'dut' permanently.
19:00:23 - DCP_1: Test step 11: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:00:28 - DCP_1: Test step 12: Requesting ARP for IP - Address: 192.168.0.50
19:00:28 - DCP_1: Test step 13: Check the IdentifyAll response behavior.
19:00:28 - DCP_1: Test step 14: Temporarily set the ip address of the DUT to 192.168.0.51
19:00:33 - DCP_1: Test step 15: Requesting ARP for IP - Address: 192.168.0.51
19:00:33 - DCP_1: Test step 16: Check the IdentifyAll response behavior.
19:00:33 - DCP_1: Test step 17: Powering off - on the dut
19:00:39 - DCP_1: Test step 18: Waiting for the DUT to power up again.
19:02:11 - DCP_1: Test step 19: Requesting ARP for IP - Address: 192.168.0.50
19:02:11 - ERROR: Dcp: No response received.
19:02:11 - ERROR: DCP_1: Test step 20: There was an ARP received. This was not expected.
19:02:11 - DCP_1: Test step 20: DCP - DCP 1: Aborted due to errors.
19:02:11 - DCP_1: Start of test DCP - DCP 1 with VLAN-Tag
19:02:11 - DCP_1: Test step 1: Requesting ResetToFactory (reset communication parameters) of the dut
19:02:11 - DCP_1: Test step 2: Waiting for the DUT to apply the reset to factory request. [ms]: 60000
19:03:11 - DCP_1: Test step 3: Check the IdentifyAll response behavior.
19:03:11 - DCP_1: Test step 4: Powering off - on the dut
19:03:17 - DCP_1: Test step 5: Waiting for the DUT to power up again.
19:04:49 - DCP_1: Test step 6: Set the name of station to 'dut' permanently.
19:04:54 - DCP_1: Test step 7: Send an Identify.Req with the name of the DUT as filter.
19:04:54 - DCP_1: Test step 8: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:04:59 - DCP_1: Test step 9: Send a DcpGet.Req with the following parameter: NameOfStation, DeviceId, MacAddress and IpParamter.
19:04:59 - DCP_1: Test step 10: Set the name of station to 'dut' permanently.
19:05:04 - DCP_1: Test step 11: Setting the IP-Parametes (IP, Subnetmask, Gateway) of the dut permanently.
19:05:09 - DCP_1: Test step 12: Requesting ARP for IP - Address: 192.168.0.50
19:05:09 - DCP_1: Test step 13: Check the IdentifyAll response behavior.
19:05:09 - DCP_1: Test step 14: Temporarily set the ip address of the DUT to 192.168.0.51
19:05:14 - DCP_1: Test step 15: Requesting ARP for IP - Address: 192.168.0.51
19:05:14 - DCP_1: Test step 16: Check the IdentifyAll response behavior.
19:05:14 - DCP_1: Test step 17: Powering off - on the dut
19:05:20 - DCP_1: Test step 18: Waiting for the DUT to power up again.
19:06:52 - DCP_1: Test step 19: Requesting ARP for IP - Address: 192.168.0.50
19:06:52 - ERROR: Dcp: No response received.
19:06:52 - ERROR: DCP_1: Test step 20: There was an ARP received. This was not expected.
19:06:52 - DCP_1: Test step 20: DCP - DCP 1: Aborted due to errors.
19:06:58 - Finished test case DCP - DCP 1.
19:07:02 - Starting Testcase: DCP - DCP_2
19:07:02 - Initializing Power Outlet
19:07:04 - DCP_2: Start of test DCP - DCP_2 without VLAN-Tag
19:07:04 - DCP_2: Test step 1: Requesting ResetToFactory (reset communication parameters) of the dut
19:07:04 - DCP_2: Test step 2: Waiting for the DUT to apply the reset to factory request. [ms]: 60000
19:08:04 - DCP_2: Test step 3: Check the IdentifyAll response behavior.
19:08:04 - DCP_2: Test step 4: Powering off - on the dut
19:08:10 - DCP_2: Test step 5: Waiting for the DUT to power up again.



I do not know why its not getting response of ARP command. normally when i create project in ART-Tester it can automatically get Mac address of DUT.
It seems that your device is not dealing well with restoring remanence data after a PowerOn. The expectation is, that from the temporary set IP address no ARP.Req is answered after a Power On.
Ask another Question