Why Should the Watchdog Time (F_WD_Time) Not Be More Than 130% the Minimum Time?

PS-cE
PROFINET Expert
Posts: 25
Joined: 16 Oct 2023, 05:21

Why Should the Watchdog Time (F_WD_Time) Not Be More Than 130% the Minimum Time?

Post

The PROFIsafe Profile states in section 'Adjustment of watchdog times for FSCP 3/1':
It is highly recommended that the difference between the assigned parameter value F_WD_Time and the sum (DAT, HAT, and bus transmission delays) does not exceed 30 %.
Why is this the case?
PS-cE
PROFINET Expert
Posts: 25
Joined: 16 Oct 2023, 05:21

Re: Why Should the Watchdog Time (F_WD_Time) Not Be More Than 130% the Minimum Time?

Post

PS-cE wrote: 21 Nov 2024, 15:29 The PROFIsafe Profile states in section 'Adjustment of watchdog times for FSCP 3/1':
It is highly recommended that the difference between the assigned parameter value F_WD_Time and the sum (DAT, HAT, and bus transmission delays) does not exceed 30 %.
Why is this the case?

In section 'Calculation and optimization', the formula for calculating the Safety Function Response Time (SFRT) part for PROFIsafe is given. The F_WD_Time is part of this calculation. The underlying model assumes the F_WD_Time to be within the stated 130% limit, otherwise the SFRT formula would not work anymore/would have to be adapted.