Manual-DHT Testcase

rottava
Posts: 21
Joined: 29 Jan 2025, 15:03

Manual-DHT Testcase

Post

Hello,

Of all tests performed, only one is reporting 'Inconclusive', Manual-DHT.
Screenshot 2025-05-15 160547.png
Screenshot 2025-05-15 160547.png (31.49 KiB) Viewed 9296 times
Screenshot 2025-05-15 155522.png
Screenshot 2025-05-15 155522.png (31.76 KiB) Viewed 9296 times
As a result, Certification Report shows one error. According to TCS_00000014_DHT document, page 11, "... a manual investigation shall ensure the consistency of the responses".

Question, is it ok to submit the product for certification this way? I mean, is it something critical that I have to check right now (TBH, don't really know how) or am I overthinking?

Thanks,
Luciano.
Raik.Zachmann
PROFINET Expert
Posts: 36
Joined: 19 Sep 2023, 07:37

Re: Manual-DHT Testcase

Post

rottava wrote: 15 May 2025, 21:12 Hello,

Of all tests performed, only one is reporting 'Inconclusive', Manual-DHT.

Screenshot 2025-05-15 160547.png
Screenshot 2025-05-15 155522.png

As a result, Certification Report shows one error. According to TCS_00000014_DHT document, page 11, "... a manual investigation shall ensure the consistency of the responses".

Question, is it ok to submit the product for certification this way? I mean, is it something critical that I have to check right now (TBH, don't really know how) or am I overthinking?

Thanks,
Luciano.
Hi,

the faster cycle times have to be tested using the IOC Controller "A" and manual investigation of the wireshark traces.

Best regards,
Raik