Netload test, X005 does not let see LLDP packets
Posted: 28 Oct 2023, 10:15
Hello. This is my first post.
I have some experience with PROFINET testing. I have a problem. We have two X005 SCALANCES, the part number recommended for the Netload test.
One of the switches works as expected. But the other does not work as expected. I explain myself: The standard setup for netload shoes the S7-1500 (device 'a') communicating normally with DUT and device 'c' (the ET-200). But this one switch does not capture LLDP packets, hence the test fails with this switch but passes with the other one.
For the switch that lets LLDP packets get to the capture, the LEDs in the switch are orange, whereas in the other the LEDs are green.
Why is this. Is there a way to fix or reconfigure the switch so that it allows capture of LLDP packets?
Thanks.
I have some experience with PROFINET testing. I have a problem. We have two X005 SCALANCES, the part number recommended for the Netload test.
One of the switches works as expected. But the other does not work as expected. I explain myself: The standard setup for netload shoes the S7-1500 (device 'a') communicating normally with DUT and device 'c' (the ET-200). But this one switch does not capture LLDP packets, hence the test fails with this switch but passes with the other one.
For the switch that lets LLDP packets get to the capture, the LEDs in the switch are orange, whereas in the other the LEDs are green.
Why is this. Is there a way to fix or reconfigure the switch so that it allows capture of LLDP packets?
Thanks.