Manual-DHT Testcase

Posted: 15 May 2025, 21:12
by rottava
Hello,

Of all tests performed, only one is reporting 'Inconclusive', Manual-DHT.
Screenshot 2025-05-15 160547.png
Screenshot 2025-05-15 160547.png (31.49 KiB) Viewed 9552 times
Screenshot 2025-05-15 155522.png
Screenshot 2025-05-15 155522.png (31.76 KiB) Viewed 9552 times
As a result, Certification Report shows one error. According to TCS_00000014_DHT document, page 11, "... a manual investigation shall ensure the consistency of the responses".

Question, is it ok to submit the product for certification this way? I mean, is it something critical that I have to check right now (TBH, don't really know how) or am I overthinking?

Thanks,
Luciano.

Re: Manual-DHT Testcase

Posted: 23 May 2025, 11:05
by Raik.Zachmann
rottava wrote: 15 May 2025, 21:12 Hello,

Of all tests performed, only one is reporting 'Inconclusive', Manual-DHT.

Screenshot 2025-05-15 160547.png
Screenshot 2025-05-15 155522.png

As a result, Certification Report shows one error. According to TCS_00000014_DHT document, page 11, "... a manual investigation shall ensure the consistency of the responses".

Question, is it ok to submit the product for certification this way? I mean, is it something critical that I have to check right now (TBH, don't really know how) or am I overthinking?

Thanks,
Luciano.
Hi,

the faster cycle times have to be tested using the IOC Controller "A" and manual investigation of the wireshark traces.

Best regards,
Raik