PROFISAFE Time disconnection

Posted: 12 Sep 2025, 10:00
by Tristan_Brest
Hello PROFINET experts :) ,

I am working on an architecture on which i need to send an Emergency Stop Signal throught a Black Chanel communication system (trought antenna).

On the machine side, I have a SIEMENS PLC (S71500 family), which activate the power of the machine. On the other side, I have a remote control for the operator, with an emergency stop. My main problem is that I need to be robust to disconnection between machine and REMOTE Control Up to 10s.

It means that if the link between both is broken for less than 10s, my machine have to not be stopped.

I have tried with a PROFISAFE link, but it seems that I am limited to a disconnection time of 1,92s, linked to the PROFINET Protocol. Are you agree with this value ?

Thank you

Tristan

Re: PROFISAFE Time disconnection

Posted: 12 Sep 2025, 12:10
by PS-cE
Tristan_Brest wrote: 22 Sep 2025, 09:27
PS-cE wrote: 12 Sep 2025, 17:18
Tristan_Brest wrote: 12 Sep 2025, 10:00 Hello PROFINET experts :) ,

I am working on an architecture on which i need to send an Emergency Stop Signal throught a Black Chanel communication system (trought antenna).

On the machine side, I have a SIEMENS PLC (S71500 family), which activate the power of the machine. On the other side, I have a remote control for the operator, with an emergency stop. My main problem is that I need to be robust to disconnection between machine and REMOTE Control Up to 10s.

It means that if the link between both is broken for less than 10s, my machine have to not be stopped.

I have tried with a PROFISAFE link, but it seems that I am limited to a disconnection time of 1,92s, linked to the PROFINET Protocol. Are you agree with this value ?

Thank you

Tristan
The upper limit on the PROFIsafe watchdog time (F_WD_Time) is 65535 milliseconds (so roughly a little over 1 minute), which is supported by S7-1500 F-PLCs and also many F-Devices.

You might see a lower, limited upper watchdog time on an F-Device if such defined by its vendor and defined in, e.g., the GSD.

Best Regards,
Christian
Hello Christian,

Thank you for your answer ,but I didn't see it, sorry.
I understand in your message that it could be possile for your understanding.
I am just setting up a moke up to test it, but it seems that I am limited to 1,92s with the PROFINET layer. I mean, in the Real Time settings of my PROFISAFE device, I have to configure the IO cycle and the WatchDog time. If i can choose an update time up to 512ms, i can't set a watchdog time more than 1,92s.
I continue to investiguate. :)

Thank you
Tristan

Hello Tristan,

Just to make sure I understand this correctly: The Safety Function Response Time (SFRT) of the safety function (or at least the communication part of the SFRT) is 10 seconds?

Best Regards,
Christian

Re: PROFISAFE Time disconnection

Posted: 12 Sep 2025, 17:18
by PS-cE
Tristan_Brest wrote: 12 Sep 2025, 10:00 Hello PROFINET experts :) ,

I am working on an architecture on which i need to send an Emergency Stop Signal throught a Black Chanel communication system (trought antenna).

On the machine side, I have a SIEMENS PLC (S71500 family), which activate the power of the machine. On the other side, I have a remote control for the operator, with an emergency stop. My main problem is that I need to be robust to disconnection between machine and REMOTE Control Up to 10s.

It means that if the link between both is broken for less than 10s, my machine have to not be stopped.

I have tried with a PROFISAFE link, but it seems that I am limited to a disconnection time of 1,92s, linked to the PROFINET Protocol. Are you agree with this value ?

Thank you

Tristan
The upper limit on the PROFIsafe watchdog time (F_WD_Time) is 65535 milliseconds (so roughly a little over 1 minute), which is supported by S7-1500 F-PLCs and also many F-Devices.

You might see a lower, limited upper watchdog time on an F-Device if such defined by its vendor and defined in, e.g., the GSD.

Best Regards,
Christian

Re: PROFISAFE Time disconnection

Posted: 18 Sep 2025, 17:19
by Tristan_Brest
Tristan_Brest wrote: 22 Sep 2025, 09:27
PS-cE wrote: 12 Sep 2025, 17:18
Tristan_Brest wrote: 12 Sep 2025, 10:00 Hello PROFINET experts :) ,

I am working on an architecture on which i need to send an Emergency Stop Signal throught a Black Chanel communication system (trought antenna).

On the machine side, I have a SIEMENS PLC (S71500 family), which activate the power of the machine. On the other side, I have a remote control for the operator, with an emergency stop. My main problem is that I need to be robust to disconnection between machine and REMOTE Control Up to 10s.

It means that if the link between both is broken for less than 10s, my machine have to not be stopped.

I have tried with a PROFISAFE link, but it seems that I am limited to a disconnection time of 1,92s, linked to the PROFINET Protocol. Are you agree with this value ?

Thank you

Tristan
The upper limit on the PROFIsafe watchdog time (F_WD_Time) is 65535 milliseconds (so roughly a little over 1 minute), which is supported by S7-1500 F-PLCs and also many F-Devices.

You might see a lower, limited upper watchdog time on an F-Device if such defined by its vendor and defined in, e.g., the GSD.

Best Regards,
Christian
Hello Christian,

Thank you for your answer ,but I didn't see it, sorry.
I understand in your message that it could be possile for your understanding.
I am just setting up a moke up to test it, but it seems that I am limited to 1,92s with the PROFINET layer. I mean, in the Real Time settings of my PROFISAFE device, I have to configure the IO cycle and the WatchDog time. If i can choose an update time up to 512ms, i can't set a watchdog time more than 1,92s.
I continue to investiguate. :)

Thank you
Tristan

Hello, thank you very much for your answer.

I 'm sorry, but I don't know what is the SFRT :(
I mean, I just know that if the connection is good between the remote control and the PLC, and that en emergency stop is pushed, i need to stop immediatly.
But, also, I don't have to stop the machine if the communication is broken for less than 10s. During this 10s, if the communication do not come back, I assume that i do not know the emergency stop signal and I don't stop the machine.

Hope this could help you to understand my question.

Thank you
Regards
Tristan

Re: PROFISAFE Time disconnection

Posted: 22 Sep 2025, 09:27
by Tristan_Brest
PS-cE wrote: 12 Sep 2025, 17:18
Tristan_Brest wrote: 12 Sep 2025, 10:00 Hello PROFINET experts :) ,

I am working on an architecture on which i need to send an Emergency Stop Signal throught a Black Chanel communication system (trought antenna).

On the machine side, I have a SIEMENS PLC (S71500 family), which activate the power of the machine. On the other side, I have a remote control for the operator, with an emergency stop. My main problem is that I need to be robust to disconnection between machine and REMOTE Control Up to 10s.

It means that if the link between both is broken for less than 10s, my machine have to not be stopped.

I have tried with a PROFISAFE link, but it seems that I am limited to a disconnection time of 1,92s, linked to the PROFINET Protocol. Are you agree with this value ?

Thank you

Tristan
The upper limit on the PROFIsafe watchdog time (F_WD_Time) is 65535 milliseconds (so roughly a little over 1 minute), which is supported by S7-1500 F-PLCs and also many F-Devices.

You might see a lower, limited upper watchdog time on an F-Device if such defined by its vendor and defined in, e.g., the GSD.

Best Regards,
Christian
Hello Christian,

Thank you for your answer ,but I didn't see it, sorry.
I understand in your message that it could be possile for your understanding.
I am just setting up a moke up to test it, but it seems that I am limited to 1,92s with the PROFINET layer. I mean, in the Real Time settings of my PROFISAFE device, I have to configure the IO cycle and the WatchDog time. If i can choose an update time up to 512ms, i can't set a watchdog time more than 1,92s.
I continue to investiguate. :)

Thank you
Tristan

Re: PROFISAFE Time disconnection

Posted: 22 Sep 2025, 14:17
by PS-cE
Tristan_Brest wrote: 22 Sep 2025, 09:27
[...]

Hello Christian,

Thank you for your answer ,but I didn't see it, sorry.
I understand in your message that it could be possile for your understanding.
I am just setting up a moke up to test it, but it seems that I am limited to 1,92s with the PROFINET layer. I mean, in the Real Time settings of my PROFISAFE device, I have to configure the IO cycle and the WatchDog time. If i can choose an update time up to 512ms, i can't set a watchdog time more than 1,92s.
I continue to investiguate. :)

Thank you
Tristan
It seems the limitations you are seeing are specific to your F-Device. They are not based on limitations in the underlying specifications. It might be a good idea to check back with the vendor of your device.

Re: PROFISAFE Time disconnection

Posted: 22 Sep 2025, 14:21
by PS-cE
Tristan_Brest wrote: 18 Sep 2025, 17:19
[...]

Hello, thank you very much for your answer.

I 'm sorry, but I don't know what is the SFRT :(
I mean, I just know that if the connection is good between the remote control and the PLC, and that en emergency stop is pushed, i need to stop immediatly.
But, also, I don't have to stop the machine if the communication is broken for less than 10s. During this 10s, if the communication do not come back, I assume that i do not know the emergency stop signal and I don't stop the machine.

Hope this could help you to understand my question.

Thank you
Regards
Tristan
You might want to investigate this further. In the scenario you describe, it could happen that somebody pressed the emergency stop button, but because of the 10 second communication interruption that you allow, nothing happens for 10 seconds. So the machine keeps working for 10 seconds before it stops. Please investigate with a safety manager whether this is really what is needed in your scenario. You might also want to consult ISO 13850.